NC-v2.2 EAc4: Enhanced Refrigerant Management 1 point

See all forum discussions about this credit »

Credit achievement rate

XX%

Upgrade to LEEDuser Premium to see how many projects achieved this credit. Try it free »

LEEDuser’s viewpoint

Frank advice from LEED experts

LEED is changing all the time, and every project is unique. Even seasoned professionals can miss a critical detail and lose a credit or even a prerequisite at the last minute. Our expert advice guides our LEEDuser Premium members and saves you valuable time.

Credit language

USGBC logo

© Copyright U.S. Green Building Council, Inc. All rights reserved.

Requirements

Option 1
Do not use refrigerants. OR
Option 2
Select refrigerants and HVAC&R that minimize or eliminate the emission of compounds that contribute to ozone depletion and global warming. The base building HVAC&R equipment shall comply with the following formula, which sets a maximum threshold for the combined contributions to ozone depletion and global warming potential: LCGWP + LCODP x 105 ≤ 100 Where: LCODP = [ODPr x (Lr x Life +Mr) x Rc]/Life LCGWP = [GWPr x (Lr x Life +Mr) x Rc]/Life LCODP: Lifecycle Ozone Depletion Potential (lbCFC11/Ton-Year) LCGWP: Lifecycle Direct Global Warming Potential (lbCO2/Ton-Year) GWPr: Global Warming Potential of Refrigerant (0 to 12,000 lbCO2/lbr) ODPr: Ozone Depletion Potential of Refrigerant (0 to 0.2 lbCFC11/lbr) Lr: Refrigerant Leakage Rate (0.5% to 2.0%; default of 2% unless otherwise demonstrated) Mr: End-of-life Refrigerant Loss (2% to 10%; default of 10% unless otherwise demonstrated) Rc: Refrigerant Charge (0.5 to 5.0 lbs of refrigerant per ton of Gross ARI rated cooling capacity) Life: Equipment Life (10 years; default based on equipment type, unless otherwise demonstrated) For multiple types of equipment, a weighted average of all base building level HVAC&R equipment shall be applied using the following formula: [ ∑ (LCGWP + LCODP x 105) x Qunit ] / Qtotal ≤ 100 Where: Qunit = Gross ARI rated cooling capacity of an individual HVAC or refrigeration unit (Tons) Qtotal = Total Gross ARI rated cooling capacity of all HVAC or refrigeration Small HVAC units (defined as containing less than 0.5 lbs of refrigerant), and other equipment such as standard refrigerators, small water coolers, and any other cooling equipment that contains less than 0.5 lbs of refrigerant, are not considered part of the “base building” system and are not subject to the requirements of this credit. AND Do not install fire suppression systems that contain ozone-depleting substances (CFCs, HCFCs or Halons). See all forum discussions about this credit »

What does it cost?

Cost estimates for this credit

On each BD+C v4 credit, LEEDuser offers the wisdom of a team of architects, engineers, cost estimators, and LEED experts with hundreds of LEED projects between then. They analyzed the sustainable design strategies associated with each LEED credit, but also to assign actual costs to those strategies.

Our tab contains overall cost guidance, notes on what “soft costs” to expect, and a strategy-by-strategy breakdown of what to consider and what it might cost, in percentage premiums, actual costs, or both.

This information is also available in a full PDF download in The Cost of LEED v4 report.

Learn more about The Cost of LEED v4 »

Checklists

Step by step to LEED certification

LEEDuser’s checklists walk you through the key action steps you need to earn a credit, including how to avoid common pitfalls and save money.

See all forum discussions about this credit »

Documentation toolkit

The motherlode of cheat sheets

LEEDuser’s Documentation Toolkit is loaded with calculators to help assess credit compliance, tracking spreadsheets for materials, sample templates to help guide your narratives and LEED Online submissions, and examples of actual submissions from certified LEED projects for you to check your work against. To get your plaque, start with the right toolkit.

Credit achievement rate

XX%

Upgrade to LEEDuser Premium to see how many projects achieved this credit. Try it free »

Get the inside scoop

Our editors have written a detailed analysis of nearly every LEED credit, and LEEDuser premium members get full access. We’ll tell you whether the credit is easy to accomplish or better left alone, and we provide insider tips on how to document it successfully.

USGBC logo

© Copyright U.S. Green Building Council, Inc. All rights reserved.

Requirements

Option 1
Do not use refrigerants. OR
Option 2
Select refrigerants and HVAC&R that minimize or eliminate the emission of compounds that contribute to ozone depletion and global warming. The base building HVAC&R equipment shall comply with the following formula, which sets a maximum threshold for the combined contributions to ozone depletion and global warming potential: LCGWP + LCODP x 105 ≤ 100 Where: LCODP = [ODPr x (Lr x Life +Mr) x Rc]/Life LCGWP = [GWPr x (Lr x Life +Mr) x Rc]/Life LCODP: Lifecycle Ozone Depletion Potential (lbCFC11/Ton-Year) LCGWP: Lifecycle Direct Global Warming Potential (lbCO2/Ton-Year) GWPr: Global Warming Potential of Refrigerant (0 to 12,000 lbCO2/lbr) ODPr: Ozone Depletion Potential of Refrigerant (0 to 0.2 lbCFC11/lbr) Lr: Refrigerant Leakage Rate (0.5% to 2.0%; default of 2% unless otherwise demonstrated) Mr: End-of-life Refrigerant Loss (2% to 10%; default of 10% unless otherwise demonstrated) Rc: Refrigerant Charge (0.5 to 5.0 lbs of refrigerant per ton of Gross ARI rated cooling capacity) Life: Equipment Life (10 years; default based on equipment type, unless otherwise demonstrated) For multiple types of equipment, a weighted average of all base building level HVAC&R equipment shall be applied using the following formula: [ ∑ (LCGWP + LCODP x 105) x Qunit ] / Qtotal ≤ 100 Where: Qunit = Gross ARI rated cooling capacity of an individual HVAC or refrigeration unit (Tons) Qtotal = Total Gross ARI rated cooling capacity of all HVAC or refrigeration Small HVAC units (defined as containing less than 0.5 lbs of refrigerant), and other equipment such as standard refrigerators, small water coolers, and any other cooling equipment that contains less than 0.5 lbs of refrigerant, are not considered part of the “base building” system and are not subject to the requirements of this credit. AND Do not install fire suppression systems that contain ozone-depleting substances (CFCs, HCFCs or Halons).

XX%

Upgrade to LEEDuser Premium to see how many projects achieved this credit. Try it free »

Got the gist of EAc4 but not sure how to actually achieve it? LEEDuser gives step-by-step help. Premium members get:

  • Checklists covering all the key action steps you'll need to earn the credit.
  • Hot tips to give you shortcuts and avoid pitfalls.
  • Cost tips to assess what a credit will actually cost, and how to make it affordable.
  • Ideas for going beyond LEED with best practices.
  • All checklists organized by project phase.
  • On-the-fly suggestions of useful items from the Documentation Toolkit and Credit Language.

In the end, LEED is all about documentation. LEEDuser’s Documentation Toolkit, for premium members only, saves you time and helps you avoid mistakes with:

  • Calculators to help assess credit compliance.
  • Tracking spreadsheets for materials purchases.
  • Spreadsheets and forms to give to subs and other team members.
  • Guidance documents on arcane LEED issues.
  • Sample templates to help guide your narratives and LEED Online submissions.
  • Examples of actual submissions from certified LEED projects.
See all LEEDuser forum discussions about this credit » Subscribe to new discussions about NC-v2.2 EAc4