Recertification

44 replies [Last post]
Aug 03 2010 Guest
1884 Thumbs Up
Post a Comment

  

44 Comments

0
0
Rachel Nicely
Feb 28 2013
LEEDuser Member
88 Thumbs Up

Recertification EAc4

I'm having trouble with my recertification template for credit EAc4. When I input the total RECs purchased (only using off-site renewable energy) and the total energy site usage, it is telling me that I have purchased 100% green power. Based on my calculations, I believe that I only purchased 50%. Is there a different calculation to use? Or is the template faulty?

1
1
0
Alicia Chu Sustainability Advisor, Healthy Buildings Feb 28 2013 Guest 62 Thumbs Up

If you are referring to the percentage that is calculated within the table, then this is referring to the percent over the performance period only. Additionally, the amount purchased should be for the designated performance period only (not the full 2 year contract). I'm looking at a v05 form so maybe they've fixed the bug? If you need a form update, you can request one by clicking on the feedback link at the top of the website.

Post a Reply
0
0
Alicia Chu Sustainability Advisor Healthy Buildings
Aug 15 2012
Guest
62 Thumbs Up

Recertification LEED Online v3 Registration

Has anyone successfully registered a project for recertification that was previously certified under LEED Online v3? I was just informed by the USGBC representative that I needed to register the project as if it was not initially certified under v3. My hope was that certain project items would transfer over into the recertification project but it doesn't seem like the case.

1
1
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Aug 15 2012 LEEDuser Expert 1783 Thumbs Up

Alicia

Go back and discuss this with GBCI. I think your snag may be due to the fact that LEED on LIne can't 'transfer' all the original documentation from the first certification straight into all the credits in the re-certification. (It's classed as a 'certification' with each credit having the option button that shows that the building was originally certified under LEED EB, NC, CS)....which means...then you'll need to review each credit and upload all the documents again. In some ways this is sensible as it will make you look through the credit support documents and understand any shortfalls that you may get with the re-cert.

Post a Reply
0
0
Alicia Chu Sustainability Advisor Healthy Buildings
Jul 20 2012
Guest
62 Thumbs Up

New Recertification Guidance!

New guidance for Existing Buildings recertification has been posted! You can find it here: https://www.usgbc.org/ShowFile.aspx?DocumentID=19201

This document is meant to replace all previously released temporary guidance, but it doesn't discuss what to do with credits not previously awarded in the initial certification.

1
7
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Jul 20 2012 LEEDuser Expert 1783 Thumbs Up

Any credits not previously awarded are treated like 'new'...i.e. 3 month performance data needed. (However during the recertification performance period...4 to 5 years, it would be nice if building operators were already taking data down to show that the building is advancing over the whole performance rather than just the last 3 months)

2
7
0
Chris Munn Director, National Operations, Chelsea Group, Ltd. Jul 20 2012 LEEDuser Member 1302 Thumbs Up

Hooray! This guidance has been long awaited. I'm very excited to see we finally have a clear document to reference in our Certification maintenance. Thanks to all who contributed to this document.

3
7
0
Alicia Chu Sustainability Advisor, Healthy Buildings Jul 21 2012 Guest 62 Thumbs Up

Barry - Thank you for your response! I assumed that was the case. The guidance also defines recertification as any "Subsequent application(s) to the LEED for Existing Buildings: Operation Maintenance program after receiving an initial LEED for Existing Buildings certification under any version." Does this mean we can now recertify buildings that were previously certified under LEED EB 2.0? The previous guidance specifically stated that this would not qualify for recertification.

4
7
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Jul 21 2012 LEEDuser Expert 1783 Thumbs Up

Any version of EB, even back to pilots can now re-certify with these guidelines provided that they satisfy the 5 year rule. Good luck

5
7
0
Alicia Chu Sustainability Advisor, Healthy Buildings Jul 21 2012 Guest 62 Thumbs Up

I have to say, I am very glad that the USGBC really kept the owner's best interest in mind with these guidelines!

6
7
0
Margaret Sonoda Sep 18 2012 LEEDuser Member 4 Thumbs Up

The recertification guidelines "temporary" or otherwise have apparently been removed from the website. When you go to the link posted here a message pops up that says "Stay Tuned! Guidelines available September 2012" I've searched and searched and can't find recertification guidelines anywhere and submitted an email inquiry today to GBCI asking when they expect to post the guidelines. We've registered our LEED EB Gold corporate headquarters for recertification but it's all pretty confusing at this point.

7
7
0
Gwen Sheinfeld Director, Corporate Sustainability , Healthy Buildings Nov 14 2012 LEEDuser Member 51 Thumbs Up

LEED EBO&M Recertification Guidance as of 11/07/2012

https://new.usgbc.org/resources/leed-existing-buildings-operations-amp-m...

Cheers!

Post a Reply
0
0
Chris Munn Director, National Operations Chelsea Group, Ltd.
Feb 14 2012
LEEDuser Member
1302 Thumbs Up

Recertify- post 5 years?

According to the guidance I've seen from LEED, your performance period for recertification is from the time you were certified initially up until the time you submit for for recertification. Therefore if you wait 5 years, you are expected to provide 5 years of data. Well, what if you simply wait until that 5 years expires, and then simply start again with 3 month performance periods? That seems to make more sense than gathering 5 years of data.

1
1
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Feb 14 2012 LEEDuser Expert 1783 Thumbs Up

It's certainly an option, except that during that 5 years we have well seen at least two updates to LEED. The purpose of recert is to make a seamless transition between the different years of operations. By recertifying at least ever two years rather than five you will be able to make use of almost all the existing forms and support documentation that you used initially. Yes you are right the support paperwork is a nightmare especially if you have no documents being gathered over the years and letting the certification lapse is an option. However is this really want we want to do. Our original intention was to show that over the years buildings can provide the support data that shows that they have maintained their high performance status and are worthy of displaying the EB plaque. By letting the EB lapse you are not showing this only that for a three month period you'd complied. This discussion is not really about certification, it's really about data acquisition and maintainance

Post a Reply
0
0
Chris Munn Director, National Operations Chelsea Group, Ltd.
Feb 14 2012
LEEDuser Member
1302 Thumbs Up

Recertification Guidance

Is the USGBC ever going to release guidance on recertification? I've been told for over a year and a half now to sit tight, because recertification guidance is on the way. I still have yet to see anything on the website. I've been project manager for a number of certified EB O&M buildings, and they are all requesting guidance on how to maintain their documentation and recertify. I've been telling them that guidance is on the way, but still nothing. All I've heard is that once you're certified, your Performance Period for recertification starts the day you are certified. Therefore if you were certified four years ago, then you need to collect fours years of data for any credits you achieved initially. Besides that, there is still a lot of gray area. Are properties expected to conduct Energy Audits on an annual basis? Do the ASHRAE 62 outdoor air readings have to be measured again? If so, how often, annually? Once during the performance period? Its become very frustrating waiting on guidance, and I'm afraid that it is hurting the Certification process. Without proper guidance, I fear that some of these properties will let some of the aspects go by the wayside. The market is out there for recertification. But without proper guidance from the USGBC, it is becoming difficult to keep these properties on task. If anyone can provide insight on recertification and recertification resources, it would be greatly appreciated.

1
3
0
Tristan Roberts LEED AP BD+C, Editorial Director – LEEDuser, BuildingGreen, Inc. Feb 17 2012 LEEDuser Moderator

Chris, I heard that USGBC is actively working on this and expects something out by mid- to late-spring. By "something" I mean not only guidance but LEED Online functionality. Stay posted!

2
3
0
Asa Posner Senior Sustainability Consultant, Sustainable Investment Group (SIG) Jun 07 2012 LEEDuser Member 546 Thumbs Up

yo! its summer, whats the update on recert guidance?

do we need to perform the IBEAM audit (IEQc1.1) every year?
do we need to submit new data for WEc3?
WEc4?
EAc6?
IEQc1.4?

3
3
0
Amanda Doenges Sustainability & Energy Services Engineer, Heapy Engineering Jul 11 2012 Guest 8 Thumbs Up

Here is the Recertification Guide. It helps a bit, but still has a few gray areas: https://www.usgbc.org/ShowFile.aspx?DocumentID=19201

Post a Reply
0
0
Chi-Chung Sue Steven Leach International Asia Inc. Taiwan Branch
Oct 25 2011
LEEDuser Member
3481 Thumbs Up

Re certification Process for IEQc2.1

Our project recently been awarded, and we are now ask by owner, how to get prepare for re certification process. one interesting topic that we bring onto the table is IEQc2.1 (occupant survey).
based on our experienced in conducting occupant surveys process, we took almost 5 months to complete the whole process from end to end.
Our building have 81 difference tenants, and average daily occupant coming to work into our office tower is 11,000 people. as if we to conduct the survey according to ASHRAE 55 -2004 recommendation (once every 6 months). If were to follow the recommendation, we anticipated to use up great amount of human resources yet create some discomfort level to the tenants. Has anyone encounter this issue before during re certification preparation with building owner?

1
2
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Oct 26 2011 LEEDuser Expert 1783 Thumbs Up

I'd contact GBCI and get a clear answer as previously this need only be repeated every TWO years (unless of course you had major faults highlighted in the survey that required operational or physical changes to the building). In any case with that amount of people I'd take the 'average' number option rather than trying to do the whole 11,000.

2
2
0
Chi-Chung Sue Steven Leach International Asia Inc. Taiwan Branch Nov 01 2011 LEEDuser Member 3481 Thumbs Up

Hi Barry,
thanks for the input. When was your last discussion with GBCI? i hope they still stick with 2 years per survey. The previous survey result is ok, doesn't have major issues, only that, it really a tiring process if were to follow ASHRAE 55 requirement. Ya, though is 11,000 people, we only took 30% of the actual total occupant.

Post a Reply
0
0
Sheryl Swartzle LEED administration TLC Engineering for Architecture
Oct 24 2011
LEEDuser Member
269 Thumbs Up

Recertification of EBOM project

We received initial EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. v2 certification in April 2010. We are now pursuing recertification. Do we have to wait 2 years from the April 2010 date before submitting our recertification to GBCI for review? Would our performance period for recertification start from date of original certification or from end date of performance period of original certification? What should the time span of the performance period be? Thanks for any assistance.

1
1
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Oct 25 2011 LEEDuser Expert 1783 Thumbs Up

You can re-certify as soon as you like or any time up to 5 years. The recert starts the day you get the original certification (see your email from the GBCI). [The building was not 'certified' until the GBCI says it was]

Post a Reply
0
0
Paul Loesch Environmental Sustainability Intern Aramark - Baylor University
Jun 02 2011
Guest
80 Thumbs Up

Requirements for Recertification

Our project initially certified in June 2009 under LEED EB v2.0. We have registered for recertification under LEED EB+OM 2009.

What are the requirements for us to recertify? Do we have to resubmit documentation of each individual credit or just for the prerequisites?

Submitting for each individual credit is essentially starting over considering the significant changes to the rating system. In this case, how would we handle the performance period for credits and prerequisites that did not previously exist?

Reference guide states performance period for credits not earned during initial certification is the initial performance period. It is basically impossible for them to expect us to have policies in place or be collecting data for credits/prereqs that were did not exist during this period.

I have requested clarification from GBCI and expect a response in the next few weeks. Any advice in the meantime would be very much appreciated. Any one gone through recertification of a EB v2.0 project to EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. 2009?

1
5
0
Alicia Chu Sustainability Advisor, Healthy Buildings Jun 02 2011 Guest 62 Thumbs Up

Paul - according to a document issued by the GBCI titled "Temporary Guidance for Recertification under LEED for Existing Buildings: Operations & Maintenance," project originally certified under EB v2.0 are ineligible for recertification under LEED EB:O&M and would need to first complete initial certification under EB:O&M. With that said, it would make sense to treat your "recertifcation" project as an initial certification project.

I hope the GBCI responds to you with a more streamlined approach though. I'm sure everyone on this topic would greatly appreciate any additional information the GBCI would provide!

2
5
0
Paul Loesch Environmental Sustainability Intern, Aramark - Baylor University Jun 03 2011 Guest 80 Thumbs Up

Thanks for your insights Alicia! This seems to be the consensus among people I have spoken with. Only 2 years have passed since our initial certification, it is frustrating to be starting over completely after such a short time, but that looks to be the reality.

3
5
0
Paul Loesch Environmental Sustainability Intern, Aramark - Baylor University Jul 08 2011 Guest 80 Thumbs Up

UPDATE: Received response from GBCI on our project. Basically, because we are recertifying a LEED EB building to the new LEED EB+OM standards, we should treat it as an "Initial" certification under LEED EB+OM as Alicia suggested. Performance period will start anew and will not be: the period for initial certification or the time in between initial and recertification, as had previously been suggested also.

I am surprised this issue has not gotten more attention on this forum. Other than responses to very specific questions submitted to GBCI, there exists NO accurate information on a LEED EB to LEED EB+OM recertification. This includes the "Temporary Guidance for Recertification..." document. It does suggest that we were not eligible for recertification under EB+OM, but did not give any further instruction, especially on the performance period.

4
5
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Oct 25 2011 LEEDuser Expert 1783 Thumbs Up

I find this an interesting subject as many buildings that went LEED EB did so under v2...however if you registered under EB v3 for re-cert then the differential between the credits may pose a major problem. In legal reality if you hold a registration for re-cert under EB 2008, then really GBCI should honour that...however if they 'demand' that you up to v3 and they don't charge for the upgrade you then have two choices. 1. muscle the building through a v3, or 2. request an pass on recert and complete an 'initial' certification in v3.

5
5
0
Chris Munn Director, National Operations, Chelsea Group, Ltd. Feb 15 2012 LEEDuser Member 1302 Thumbs Up

Where can this "Temporary Guidance for Recertification under LEED for Existing Buildings: Operations & Maintenance" be found? I can't seem to find it online anywhere.

Post a Reply
0
0
Chi-Chung Sue Steven Leach International Asia Inc. Taiwan Branch
Apr 10 2011
LEEDuser Member
3481 Thumbs Up

Recertification

One of our EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. projects has been submitted for review, and we'd like to confirm the list of items that needs to be tracked thereafter for the recertification in the future.

- Per the EBOM reference guide, the recertification can take place as late as 5 years later. If that's the case, the performance period would be the entirety of the 5 years. Taking MRc5 - Food Purchasing for example, do all food and drink purchases for the duration of 5 years need to be tracked and documented for the recertification submittal?

- Does the period of 5 years start right after the project is submitted for review or right after the project receives LEED certification?

If any one can please shed some lights, your help would be much appreciated.

1
7
0
Dan Ackerstein Principal, Ackerstein Sustainability, LLC Apr 24 2011 LEEDuser Expert 6618 Thumbs Up

Jason - There is not a whole lot of public guidance on recertification yet, but if I were advising a project, my answers would be:
- Yes; purchases should be tracked for the duration. EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. is predicated on the concept that without data collection and tracking, you simply don't know whats happening in a building. The USGBC believes that the value in this tracking will outweigh the burdens. So the expectation is that once you've developed a tracking system for purchasing, waste, etc..., its permanent. And that such a system will easily allow for providing summary data at any point in time for reporting to USGBC or anyone else. That doesn't necessarily mean that the USGBC will expect you to provide documentation for all 5 years, but they reserve the right to do so.
- The 5 year clock 'should' start running at the end of your performance period. I would assume exceptions would be made for things that change via the review process, but that's the safe bet.

Lots of unanswered questions about recertification though. I wrestle with these often and look forward to hearing more about the USGBCs conclusions.

Hope that helps,

Dan

2
7
0
Chi-Chung Sue Steven Leach International Asia Inc. Taiwan Branch Apr 25 2011 LEEDuser Member 3481 Thumbs Up

Dan, thanks very much for your detailed comments. I agree with your points, and the 5-year period starting from the end of performance period would actually make more sense!

3
7
0
Jared Silliker Owner, Silliker + Partners May 25 2011 LEEDuser Member 729 Thumbs Up

I'm starting some planning in this realm as well. Water and energy are musts. But on the purchasing and waste side, is anything required? Or is just based on which credits you wish to earn? For instance, if we earned MRc4 already, I suspect we need to keep documenting those purchases in order to retain the point during recertification ... yes? But could we choose to let it lapse? What about something like MERVMinimum efficiency reporting value. 13 filters ... do we have to document those purchases over 5 years?

Am I missing any other big ticket items?

4
7
0
Dan Ackerstein Principal, Ackerstein Sustainability, LLC May 26 2011 LEEDuser Expert 6618 Thumbs Up

Jared I think the expectation is that for any credit you earn in your initial certification, you would either maintain documentation for that credit for the next X years (X being less than or = to 5), or let it lapse. I don't think its likely that USGBC will allow you to re-earn a credit if there is a lapse in performance over the 5 year period. The mechanics of that can get messy and uncertain (for example, is performance measured over the full time period, or does it need to be measured annually and meet the threshold each year within the X year period - those two things could be very different . . . ) but in the big picture, continue tracking and documenting all the credits you've earned. Theoretically, if EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. is well-designed, that tracking should be inherently valuable for ensuring the ongoing success of your sustainability program. . .

Hope that helps,
Dan

5
7
0
Jared Silliker Owner, Silliker + Partners May 28 2011 LEEDuser Member 729 Thumbs Up

Anybody know how these details can be confirmed? Agreed that tracking is valuable, but there are also many trade-offs depending on the time required for each task. We're just getting through our initial certification, so this feels like the time to build a solid list of what should be tracked and when ...

6
7
0
Tristan Roberts LEED AP BD+C, Editorial Director – LEEDuser, BuildingGreen, Inc. Jun 08 2011 LEEDuser Moderator

Jared, what details are you unsure of that you would like to confirm?

Clearly USGBC and GBCI need to provide more guidance in this area, and it's likely they will in the next couple years. However, I think Dan has a pretty good grasp on what we know right now.

7
7
0
Jared Silliker Owner, Silliker + Partners Jun 13 2011 LEEDuser Member 729 Thumbs Up

I think I'm thinking of the many little details that you're probably also referring to with "more guidance."

Many of these revolve around performance periods. Will performance periods be as low as 3 months and variable, as in the current system? Or will they all be the same, from time of original certification until the new application? I'm guessing the latter, but some odd issues could arise. For instance ... over, or during, what time frame will alternative transportation be measured? Could it be measured within the first month, but not re-checked 4 years and 11 months later?

In other cases, I'm curious if requirements will be altered slightly to better fit re-certification. Say for MRc4, the current system only calls for a purchasing plan and minimal physical purchases ... will this evolve into tracking similar to MRc1-3?

And finally, given the many plans and policies ... will efforts be made to check that they are being followed closely? For instance, the purchasing policy essentially sets the stage for MRc1-3, which my project did not pursue the first time around. Will these credits be required under re-certification?

Given our banter to date, I'm guessing these details don't exist yet ... just figured I'd keep the dialogue going.

Post a Reply
0
0
Tristan Roberts LEED AP BD+C, Editorial Director – LEEDuser BuildingGreen, Inc.
Aug 03 2010
LEEDuser Moderator

see Reference Guide

Paul, most of your questions are answered in the introductory portion of the LEED-EBOMEBOM is an acronym for Existing Buildings: Operations & Maintenance, one of the LEED 2009 rating sytems. 2009 Reference Guide. There is also some basic recertification information on the USGBC site that answers some of your questions.

Recertification does involve resubmitting credits, but it can be a streamlined process.

1
6
0
Scott Dunning Architect, HKS, Inc. Aug 16 2010 Guest 128 Thumbs Up

I've read the reference guide and would still like you to expand on the timing of recertification. Does the recertification process have to be completed within the five year limit, or can the application be made at the five year mark and the recertification process continue on into year six?

2
6
0
Tristan Roberts LEED AP BD+C, Editorial Director – LEEDuser, BuildingGreen, Inc. Aug 30 2010 LEEDuser Moderator

The LEED Reference Guide specifies that you must file for recertification at least once every five years.

My understanding is that as long as you have filed within five years, you have the time it takes your application to be processed as a grace period. This seems like it's cutting it close, though, and doesn't give you much wiggle room in correcting any issues that come up. If you've tracked and documented things through the five year period, I wouldn't think it would be a problem to get the application complete well in time.

3
6
0
Jennifer Turchin Sellen Sustainability Sep 26 2011 LEEDuser Member 145 Thumbs Up

Regarding the 5 years - does the clock start at the end of the Performance Period or the date of Certification Notification? Our project had almost a 6 month time frame from end of PP until actual certification due to the long review process so it does make a substancial difference.

Additionally, the ongoing tracking requirements still seem unclear from this string and does seem like quite a burdon on building owners to actually keep up the meticulous tracking for that length of time will be a turn off to the whole process.

4
6
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Sep 26 2011 LEEDuser Expert 1783 Thumbs Up

The clock starts the day you 'accept' the certification at whatever level you finally get. (Usually you receive a congratulatory email from the GBCI and this links to showing the project as 'certified' on the USGBC website)

5
6
0
Jennifer Turchin Sellen Sustainability Sep 26 2011 LEEDuser Member 145 Thumbs Up

So the GBCI will not ask for the tracking from the window of time from PP end date to certification? For a specific project I have in mind it was over 6 months...

6
6
0
Barry Giles Founder & CEO, USGBC LEED Faculty, LEED AP O+M, BuildingWise LLC Sep 26 2011 LEEDuser Expert 1783 Thumbs Up

Jen, I won't with-hold the info. An example would be Energy star...you can't leave out 6 months of data nor should you leave a hole in data gathering for water use, materials from a construction job etc.
What exactly are you trying to get around? How soon do you need to get re-certified, what was the date of the original certification.

Post a Reply

Start a new LEED comment thread

Jun 19 2013
Type the characters you see in this picture. (verify using audio)
Type the characters you see in the picture above; if you can't read them, submit the form and a new image will be generated. Not case sensitive.

Copyright 2013 – BuildingGreen, Inc.