I have a question regarding the site boundary in a project that will be registered for LEED-NC.  The building is existing and the entire northern half is corporate office space that will be totally renovated including new HVAC system. The southern half of the building is the company's warehouse which is connected by two corridors to a separate manufacturing building.  Could there be any problem with drawing the site boundary line directly through the
building where the office is separated from the warehouse?  The office space can be completely closed off by locking doors from the warehouse and there is no overlap in occupancy.

Thanks

48 Comments

0
0
Cynthia Estrada LEED AP BD&C SDS Architects, Inc.
Jan 19 2012
Member
134 Thumbs Up

Site Boundary

Phoebe,
The buildings must be physically distinct, and have unique addresses or names among other issues according to the Minimum Program Requirements Supplemental Guidance. Specifically, #3, there is lots of information for what you propose. Here's a link: http://www.usgbc.org/ShowFile.aspx?DocumentID=9552
Good Luck!

Log In to Reply
0
0
Daniela Castro Salgado LEED AP BD+C Edmonds International Ltd
Jan 19 2012
Guest
67 Thumbs Up

LEED Project Boundary Changes

We have a project for which we are about to submitt precertification documentation.
There were changes to the original project boundary because the street will be widened. Can we change the incially registered site area, property area and LEED project boundary?
Thank you all for your help.

1
4
0
Larry Jones Associate, Atelier Ten Jan 19 2012 Guest Expert 647 Thumbs Up

I would say yes. But you have to be sure that any site credits that are affected by this change are updated as well. For instance if you hardscape area increased, you have to take this into account for SSc5 credits.

2
4
0
Daniela Castro Salgado LEED AP BD+C , Edmonds International Ltd Jan 19 2012 Guest 67 Thumbs Up

Absolutely. Thank you Larry.
Do you know if there would be any problem if the boundary changes from Precertification to Design or Construction Review?

3
4
0
Larry Jones Associate, Atelier Ten Jan 19 2012 Guest Expert 647 Thumbs Up

As long as nothing crazy has happened to your boundary and you're still meeting MPR #3, then my guess is no. Always good to provide a brief explanation of what happened to eliminate any doubt for the reviewer.

4
4
0
Daniela Castro Salgado LEED AP BD+C , Edmonds International Ltd Jan 20 2012 Guest 67 Thumbs Up

Ok. Thank you Larry. I'll will follow your advise.

Log In to Reply
0
0
satya oktamalandi Mr. PT. Indonesia Environment Consultant
Jan 12 2012
Member
5 Thumbs Up

Urban site

Associated with LEED 2009 NC under SS credit 2, what is the definition of urban site from LEED's point of view and what are the boundaries?

1
1
0
Emily Catacchio Sustainability Specialist, Wight and Company Jan 12 2012 Moderator

Satya,

I'd reccomend reposting this question under the credit specific forum for SS credit 2 here.

Log In to Reply
0
0
Jennifer Turchin Sellen Sustainability
Nov 22 2011
Member
56 Thumbs Up

LEED Project Boundary - LEED NCv2.2

We have a hotel project that is 23 stories and was started and registered as a LEED NCv2.2 project in 2008. The design phase submittal was completed for the project and then at that time the owner placed the project on hold. The project was shelved for about a year with only the exterior of the project completed. During that time, the first floor was completed as suites (villas) and were not necessarily done to LEED standards. The remainder of the 23 stories is now being completed and we are preparing to submit for construction phase submittal. The question is how to handle the villas. Techincally, they should be excluded from the LEED boundary, but how do you do this if they were included during the design phase submittal and is USGBC/ GBCI going to allow a complete floor to be excluded from the project? If anyone has any information on a similar situation it woudl be appreciated. Thanks.

1
1
0
Emily Catacchio Sustainability Specialist, Wight and Company Nov 23 2011 Moderator

Hi Jennifer,

I doubt GBCI will allow a complete floor to be excluded from an NC project. I would reccomend contacting GBCI directly about this question.

My only thought is that you could try to start over and call your NC project an addition, in an attempt to wholly exclude that floor. But I'm not sure this would work, and I'm not sure you can start over.

Again, you should contact GBCI.

Log In to Reply
0
0
Scott Scales Project Manager Peter Gluck and Partners
Oct 27 2011
Member
5 Thumbs Up

New building overlapping an existing LEED property boundary

We are designing a new building on a site adjacent to an existing LEED v2.2 certified building (designed by another architect); both buildings are owned and operated by the same entitiy and there are multiple existing buildings (non LEED) and infrastructure. Recently, we recieved the LEED property boundary for the adjacent building and have found that our new building is currently designed partially within this boundary. Can we redefine or use a portion of the existing building's project boundary for our project without having follow the guidlines of the AGMBC? Currently there is no LEED Campus Boundary defined for this site. Any help would be appreciated.

Thanks,

Scott

1
2
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Nov 07 2011 Moderator

Scott, my understanding is that the AGMBC is an optional tool, and not something that you are required to apply in a situation like yours.

The issue I would worry about here is double-counting of site features—features that benefited the first LEED project and that will now benefit the second. I am not completely sure that this is an issue, and I can't think of an example, but it's something to watch for.

2
2
0
Cynthia Estrada LEED AP BD&C, SDS Architects, Inc. Dec 05 2011 Member 134 Thumbs Up

Scott,
Tristan is right about double counting; SSc4.4, may have an impact depending on the option used; as well as SSc5.2 if the original project had "Dedicated Open Space" within the LEED Boundary. Check also on the stormwater and water efficient lanscaping credits.

Log In to Reply
0
0
Melissa Wrolstad E4 Inc
Sep 27 2011
Member
215 Thumbs Up

Guardbooth

I have a project targeting LEED certification where the LEED Site Boundary is drawn around the parking lot surrounding the building. There is a small guard booth being constructed within this LEED Site Boundary at the entrance to the parking lot. The guard booth has a small AC unit and lighting.

Does this guard booth need to be included in LEED calculations for the building (e.g. energy modeling, lighting power density, controllability of systems, etc.) or can it be disregarded in all credit calculations?

1
1
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Nov 07 2011 Moderator

Melissa, check the LEED Minimum Program Requirements supplemental guidance. I recall that there is some allowance for disregarding auxiliary buildings like this.

Log In to Reply
0
0
Dana Murdoch
Jul 13 2011
Guest
106 Thumbs Up

Campus Reasonable Site Boundary

I am working on the documentation for a 2009 LEED-NC renovation of a single campus residence hall. I would love some clarification on a few items.

1. In the MPR 3 Language it states "LEED projects located on a campus must have project boundaries such that if all the buildings on campus become LEED certified, then 100% of the gross land area on the campus would be included with in a LEED Boundary. If this requirement is in conflict with MPR #7, then MPR #7 will take precendence."

Does this mean I have to include the whole campus in the property area of the project? Or is it more of a jigsaw puzzle idea, so as the different buildings hypothetically get LEED certified the entire campus property would eventually be included?

2. Since the residence hall is a single campus project, does it need to go through the AGMBC 2010? The application guide states that project teams may use the guidance when pursuing certification of two or more LEED Projects. I only have one project, so I don't qualify, right?

1
1
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Nov 07 2011 Moderator

Dana, I picture it as more of a jigsaw than including the whole campus in one LEED project boundary.

I don't think you're required to use the AGMBC, given that this is one project.

Log In to Reply
0
0
Veronika Sundberg Environmental Engineer - Certification Skanska Sverige AB
Jun 13 2011
Member
377 Thumbs Up

FTE/Residence number for CHILDREN at a hospital project

In the FTEFull-time equivalent (FTE) represents a regular building occupant who spends 8 hours a day (40 hours a week) in the project building. Part-time or overtime occupants have FTE values based on their hours per day divided by 8 (or hours per week divided by 40). Transient Occupants can be reported as either daily totals or as part of the FTE. Residential occupancy should be estimated based on the number and size of units. Core and Shell projects should refer to the default occupancy table in the Reference Guide appendix. All occupant assumptions must be consistent across all credits in all categories. calculation for our Hospital project we do not address the numbers of children that are visiting the hospital.
All inpatients are considered Residential and the all outpatients are calculated as visitors.

Should we consider the number of children visiting the hospital in some way and in some calculations (e.g. water calculations?) ?

Any input would be great,
Thanks /Veronika

1
1
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Nov 07 2011 Moderator

Veronika, sorry for the slow reply to your question, but could you please post this under our FTE forum? THanks!

Log In to Reply
0
0
Xavi B
Jun 07 2011
Member
1078 Thumbs Up

MPR 3.

According to MPR 3 , 1. "The LEED project boundary must include all contiguous land that is associated with and supports normal building operations for the LEED project building, including all land that was or will be disturbed for the purpose of undertaking the LEED project".
This is an existing facility and there will be a building to retrofit. There is a parking lot right next to the retrofit; it will be used for materials stock, temporary workers constructions, and construction activities for the space to retrofit. Can I leave it out of the boundary? Technically I'm not disturbing the land, since this was a parking lot and still will be after construction.
Also it is not clear to me if including existing parking capacity is required, since there will be no new parking spaces, can I just draw my boundary around the building to retrofit??
Thanks

1
7
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Jun 07 2011 Moderator

Xavi, I assume the parking lot is used for the building under normal operations? If so, it should be included within your LEED boundary. Parking is considered normal operations relative to the MPR text you quoted.

2
7
0
Xavi B Jun 09 2011 Member 1078 Thumbs Up

Thanks Tristan. What if the parking lot we are using for materials stock is for the warehouse. And there is another parking lot for the office building. Can I leave it out of the boundary even thogh it's being used for the LEED project materials stock.

3
7
0
KC Kurtz Designer-Builder, Buildsense + Studio B Architecture Jul 12 2011 Guest 68 Thumbs Up

Tristan --

Thanks to you, and others, for the wealth of information on this site!
This is the first LEED project for everyone in my office and so this site
has really been invaluable to our, as yet, less-than-perfectly-coordinated
process. Thanks again.

This is a question in a very similar vein to Xavi's above, however, even
after reading the MRP Supplemental Guidance, I
am still unclear as to where I should draw my LEED Project Boundary

Here's our situation:

We own 2 urban properties separated by a city road.

The first property,
and the one that we will develop as our C and S LEED project, is an existing
one story building (former automotive shop). We are planning on
engaging in adaptive reuseAdapted reuse is the renovation of a space for a purpose different from the original., utilizing the existing brick perimeter
walls and steel structure, for the first floor (6200 sf), and adding a
second floor (5800 sf), to create a 12,000 sf (approximate) mixed
use office building. This property is mostly zero lot line with a small
amount (350 sf) of pervious area that will be landscaped.

The second property on the other side of the city street is a parking
lot that we do not want to include in our Project Boundary --
We hope to do a separate LEED NC project here (Alternative Fueling
Station) at some point in the relatively near future. Until the Fueling
Station project is complete (and potentially beyond that point) we will
use this property as parking for property 1.

A third property, which we do not own, is a parking lot and storage buildings,
and is contiguous to the first property (LEED project building).
We have permission from the property owner (also the owner who
sold us property 1 and property 2) to use the parking lot and
storage buildings to stage material and equipment during construction.
We will also place our construction dumpster/recycling in this parking
lot during construction and we will extend our construction fence
(chainlink) onto this property. After construction, we will not use property
three for any purpose.

OK - so here's my question:

Can we draw the Project Boundary around the Project Building (property
line) only or do we need to draw it around (and therefore include in
all related credit/prerequisite calculations and documentation) property
3 (temporary staging area that we don't own)?

Many thanks.

4
7
0
David Posada Sustainability Manager, GBD Architects Jul 12 2011 Guest Expert 4067 Thumbs Up

It sounds like the third property is a previously developedPreviously developed sites are those altered by paving, construction, and/or land use that would typically have required regulatory permitting to have been initiated (alterations may exist now or in the past). Previously developed land includes a platted lot on which a building was constructed if the lot is no more than 1 acre; previous development on lots larger than 1 acre is defined as the development footprint and land alterations associated with the footprint. Land that is not previously developed and altered landscapes resulting from current or historical clearing or filling, agricultural or forestry use, or preserved natural area use are considered undeveloped land. The date of previous development permit issuance constitutes the date of previous development, but permit issuance in itself does not constitute previous development.", urban lot that is being used for temporary staging of construction activities, and is not a greenfield area that is receiving any site disturbance (as would be addressed by SSc5.1). If there are no permanent improvements to this area that will support the building on site 1, it sounds reasonable to exclude it from the LEED Site Boundary.

If the second property were to be redeveloped to provide permanent parking for the site 1 project, you would need to include it in the LEED boundary for site 1. If the local zoning requires you to provide parking, it seems like you'd have to include that area within your LEED boundary

If you are not required to provide parking, and If the second property were legitimately being used for only temporary parking for site 1, you might be able to argue it should be excluded from the site boundary, because it wouldn't be supporting the building, but then you could not use that area for any of the site credits such as SSc4.3 or SSc5 or SSc6.

GBCI gives project teams some latitude to define the boundary as they see fit, but if the parking is required it seems like you'd need to include it.

5
7
0
KC Kurtz Designer-Builder, Buildsense + Studio B Architecture Jul 13 2011 Guest 68 Thumbs Up

Thanks for your thoughtful reply David - It was very helpful.

With regards to property 2 referred to above, I am basing my understanding of Project Boundary exclusion on four pieces of information:

a) MPR Language -- "The LEED project boundary must include all contiguous land that is associated with and supports normal building operations for the LEED project building, including all land that was or will be disturbed for the purpose of undertaking the LEED project".
This parking lot is not "contiguous" to our LEED project building, but rather, it is separated by a city street (public right-of-way).

b) MPR Supplemental Guidance Revision #1 -- "When non-contiguous parcels [MAY] be included within the LEED project boundary: Non-contiguous parcels of land [MAY] be included within the LEED project boundary if the conditions below are met, and at the [PROJECT TEAM'S DISCRETION]...."

The "may" and "discretion" language implies to me that the corollary would also be true -- we may also choose NOT to include this non-contiguous land within the LEED project boundary.

c) Also, our local zoning does not require parking for this property - we are considered "Downtown Exempt".

d) It was also encouraging to hear, from you, that GBCI "gives project teams some latitude to define the boundary as they see fit...".

Also, as mentioned in my first post, we are considering developing this parking lot, using LEED NC, as an alternative fueling station (biodiesel, cng, and electric plug-ins), at some point in the future.

So, all this being said, I'd love to get a follow-up response from you on this issue of project boundaries.

Thanks again for your help!

6
7
0
David Posada Sustainability Manager, GBD Architects Jul 18 2011 Guest Expert 4067 Thumbs Up

KC,
I'd agree that the lack of a parking requirement and the MPR language on page 23 of the new guidance that says "may be included" and "at the project teams discretion" suggests you some latitude here to draw the boundary as you see appropriate. (Also check the conditions for exclusion at the top of pg 24.) I can't say for sure how a reviewer will interpret the MPRs, but your approach seems reasonable.

7
7
0
KC Kurtz Designer-Builder, Buildsense + Studio B Architecture Jul 19 2011 Guest 68 Thumbs Up

Thanks, David - fingers crossed....

Log In to Reply
0
0
Xavi B
Jun 06 2011
Member
1078 Thumbs Up

Common services

This is a retrofit of an existing office building within a medium manufacturing company. The office building is about 5000sq ft and the overall facility about
100 000sq ft. Since this is an existing space, storm water, sewer system, potable and electrical systems are shared with all the facility. Can I leave out of the boundary all those services, treatment plant, storm and sewer pipes and collectors, potable waterPotable water meets or exceeds EPA's drinking water quality standards and is approved for human consumption by the state or local authorities having jurisdiction; it may be supplied from wells or municipal water systems. pumping systems, etc. If not, I would have all the facility within the boundary, which don't make sense to me. At this moment I'm taking into account the office space and some hard-scape amenities such as sidewalks, parking lot and car entry to the property since those are used by the construction trucks. What do you think about my approach. Many thanks.

1
1
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Jun 07 2011 Moderator

Xavi, stormwater treatment infratstructure, etc. is considered as supporting normal operations and in that sense should be included in the LEED boundary for that reason. On the other hand, since that infrastructure is shared with other facilities on the site, the LEED MPR supplemental guidance gives you discretion on apportioning it with other buildings, so you should be able to do that. Just do it consistently across all credits.

Log In to Reply
0
0
James Weingarten Electrical Designer MEP Associates
Apr 14 2011
Guest
53 Thumbs Up

Waterfront sites

Can a project boundary extend into a lake? I have a Department of Natural Resources building located on a lakefront. They have a public boat landing on site. I must object to leaving the dock and boat ramp in darkness. However, if I light it I would be over the project boundary and beyond 15' would be more than .01fc.

Anyone have any LEED experience with waterfront sites project boundaries?

1
4
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. May 19 2011 Moderator

James, I would simply put the boat landing within the project boundary. I can't think of any reason why this should be avoided.

2
4
0
James Weingarten Electrical Designer, MEP Associates May 19 2011 Guest 53 Thumbs Up

Really?
Of course the boat landing is within the boundary. Can the boundary extend into a lake is the question. In the summer, the dock would need to be illuminated such that boaters can safely navigate to it. In the winter the landing is essentially a public road to provide access to the lake for ice fishing, so it should also be illuminated. Hence the reason to ask if the boundary can extend into the body of water to include the dock. Simply doing what you suggest in this matter does not address the issue.

3
4
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. May 19 2011 Moderator

I am not sure why it doesn't address the issue, or why the boundary can't extend into the water?

It sounds like it is basically part of the LEED project, so should be included. I can't think of anything in the LEED MPR's that would exclude it, although it certainly is a little unusual. Have you had any feedback from GBCI or anyone else on this?

4
4
0
David Posada Sustainability Manager, GBD Architects Jun 21 2011 Guest Expert 4067 Thumbs Up

James,
See the comment under your SSc8 post for "Waterfont sites"

Log In to Reply
0
0
deborah lucking
Jan 10 2011
Member
401 Thumbs Up

LEED boundary, property line and limit of work

Thought I'll share this with everyone. We wrote to USGBC for clarification on whether the LEED boundary should extend to the limit of work on an urban site (where we are requested by the City to do some work on curbs, sidewalks and streetlights). The MPR language was ambiguous.

USGBC replied that we should use the property line and further, that "Version 2 of the MPR Supplemental Guidance, forthcoming, will include guidance addressing this issue".

1
2
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. Jun 07 2011 Moderator
2
2
0
deborah lucking Jun 08 2011 Member 401 Thumbs Up

Tristan, many thanks! Your updates alone are worth the price of admission.

Log In to Reply
0
0
April Ambrose Sustainability Consultant: Senior Project Manager Viridian
May 03 2010
Member
1184 Thumbs Up

Contiguous LEED Boundary with parking

My current project is an addition to an existing building in a campus setting. The addition is on the southwest side of the existing building. Only the newq addition will be certified. Currently the LEED boundary is drawn through the where the addition will be the existing building. However, additional parking is required per the project and will be located to the North of the new addition on the other side of existing parking. The new parking is no where near the addition. It is unclear to me how to draw a LEED boundary to include this parking area without hurting our chances for credits such as SSC7.1 Heat Island EffectHeat island effect refers to the absorption of heat by hardscapes, such as dark, nonreflective pavement and buildings, and its radiation to surrounding areas. Particularly in urban areas, other sources may include vehicle exhaust, air-conditioners, and street equipment; reduced airflow from tall buildings and narrow streets exacerbates the effect. - Non-roof. Is it possible to separate the LEED boundary or must I include everything?

Thanks,

1
3
0
Mara Baum Healthcare Sustainable Design Leader, HOK May 12 2010 Guest Expert 1706 Thumbs Up

I would consider the parking to be a separate project and exclude the parking from the site boundary. Given that LEED prohibits you from gerrymandering or otherwise creating strange site boundaries, I think this is reasonable. However, if you are trying to achieve either SSc4.2 or 4.3 you may be forced into campus-wide parking calculations -- I'm not sure. You may want to review the LEED NC Application Guide for Multiple Buildings and On-Campus Building Projects.

2
3
0
Tristan Roberts Editorial Director – LEEDuser, BuildingGreen, Inc. May 14 2010 Moderator

I would also suggest that you check the SSc4.4 forum for a discussion on a related topic.

 

3
3
0
Jean Marais b.i.g. Bechtold INGENIEURGESELLSCHAFT MBH May 17 2010 Member 2152 Thumbs Up

I would include the parking as part of the project if it is an integral part of normal building operation. The fact that the parking addition was required says to me that it is.

"1. The LEED project boundary must include all contiguous land that is associated with and supports normal building operations for the LEED project building, including all land that was or will be disturbed for the purpose of undertaking the LEED project
2. The LEED project boundary may not include land that is owned by a party other than that which owns the LEED project unless that land is associated with and supports normal building operations for the LEED project building.." - MPR 3
http://www.usgbc.org/ShowFile.aspx?DocumentID=6715

Log In to Reply
0
0
Jean Marais b.i.g. Bechtold INGENIEURGESELLSCHAFT MBH
Mar 04 2010
Member
2152 Thumbs Up

From a theme point of view it

From a theme point of view it fits the CI better. NC has many aspects associated with what goes on outside the building, on the roof, hardscapes, stormwater, etc. CI is aimed at people who don't have much influence over things like if the roof is painted white and the hardscape is pourous. If CS was used when the building was built and assumed the tenant would build out his own HVAC distributions, then CI would be the perfect follow up. How much of the existing HVAC will be used?

1
1
0
Phoebe Kincaid Mar 04 2010 Guest 56 Thumbs Up

I really appreciate your input. I agree CI seems like it will be a better fit for the project. We excluded it originally because of the owner occupancy issue. The entire HVAC system and plumbing fixtures will be replaced for the Corp Office Renovation. Mechanicals are not shared between the Corp Office and the Warehouse.
The building is fairly old and definitely NOT build to LEED-CS. We do qualify for several Site Selection credits though and are not unduly penalized under the NC system even though we are not planning to pursue any of the credits as they pertain to roof or landscaping other than lighting.

Log In to Reply
0
0
Phoebe Kincaid
Mar 04 2010
Guest
56 Thumbs Up

Which rating system: LEED-NC or LEED-CI?

In the "LEED 2009 Supplemental MPR Guidance" document we found that there is an exception that may allow an owner occupied building to qualify under LEED-CI rather than NC (page 10). It seems we are in a bit of grey area as to which rating system to use for this project and even if either will result in an acceptable boundary line.

The building is an existing building, 100% owner occupied & managed, with horizontal separation by a party wall that separates “National Corporate Offices” from “NJ Distribution Warehouse”. Much of the warehouse is a recent addition and is largely unconditioned space and there are no plans to renovate any part of the warehouse. Renovations to the Corporate Offices will include gut interior renovation and new mechanicals.

Per checklist/scorecard, the project stands to earn approximately the same number of points under either rating system. Is there any benefit to the pursuit of LEED-NC over LEED-CI and if for some reason the requirements are interpreted as not being met after project registration for LEED-CI, may we attempt to switch to LEED-NC?

Log In to Reply
0
0
Phoebe Kincaid
Mar 02 2010
Guest
56 Thumbs Up

Site Boundary Through Existing Building

I would appreciate any input from anyone on this subject as I have had no luck getting clarification from USGBC.
Thanks

1
3
0
Shannon Gray Consultant, YRG sustainability Mar 03 2010 Guest 1581 Thumbs Up

Phoebe,

Below are the Minimum Program Requirements from the USGBC. This should help to answer your question. Let us know if you have more specific questions after reading this.

LEED projects must include the new, ground-up design and construction, or major renovation, of at least one building in its entirety.

Specific Allowed Exceptions:
Horizontally attached buildings (including additions).
Horizontally attached buildings may be certified independently provided that the following two conditions are met:
a) they are physically distinct (see definition in Glossary)
b) they have unique addresses or names.

If these conditions are not met, the structure is considered a single building and must be ertified as such.

Physically Distinct: The condition in which a building has both of the following:
a) exterior walls that are party walls or are separate from adjoining buildings by air space
b) lighting, HVAC, plumbing, and other mechanical systems that are separate from the systems of adjoining buildings. LEED project boundary lines that “slice” through party walls must not pass through any mechanical, electrical and plumbing (MEP) service infrastructure. Exceptions include buildings served by a common or shared chiller plant or heating water, or steam supply pipes (i.e., not air ducts), and only if the thermal energy serving the structure to be separated is sub‐metered.

Thanks,
Shannon

2
3
0
Xavi B Jun 07 2011 Member 1078 Thumbs Up

Hi, I have the same problem.
This is an existing warehouse attached to the office building to retrofit. There are not party walls, there is just one wall dividing the office and warehouse with window in it so the engineers could verify the process from the office. In fact it is the same roof structure for both of them, since the office space is kind of embedded in the north facade of the warehouse. The warehouse roof just continues as part of the office space. The buildings have separate systems and services.

3
3
0
David Posada Sustainability Manager, GBD Architects Jun 07 2011 Guest Expert 4067 Thumbs Up

Phoebe,
In some regions, there may be higher utility or government incentives for achieving NC instead of CI, but beyond those I can't think of any significant advantages in earning one rating vs. the other. You may find the soft costs a bit lower for CI than NC, especially for the EA credits, but you will need to account for furniture.

Xavi,
It sounds like the office may be "serving" the warehouse space since the windows are used to supervise the operations there, so it may not meet the intent of separate buildings that are horizontally attached. It is possible that reviewers would consider it a single building. You would need to submit a CIRCredit Interpretation Ruling. Used by design team members experiencing difficulties in the application of a LEED prerequisite or credit to a project. Typically, difficulties arise when specific issues are not directly addressed by LEED information/guide for clarification of the MPR to know for sure.

Log In to Reply

Copyright 2012 – BuildingGreen, Inc.